[Info-vax] Another Alpha "TEMPERATURE_VECTOR" anomaly

Stephen Hoffman seaohveh at hoffmanlabs.invalid
Wed Aug 22 23:12:41 EDT 2012


On 2012-08-22 15:24:34 +0000, Rich Jordan said:

>      RMC reports the same ~24C temperature.  Firmware is the same on
> both units, and the most recent for a DS10 (though I don't recall the
> version number); everything was upgraded to current when the systems
> were upgraded to VMS 8.3 a couple of years ago.

Seems most likely to be a displaced or detached sensor, or a wonky sensor.

Given that the environmental-level "emergency" shutdown is based on 
that thermal reading going out of spec, I'd ping the folks at HP 
services (if that's an option here) and ask them about this reading, 
and let them sort this out.  (I don't have an AlphaServer DS10 service 
manual nor the IPB handy to check that.)  If that thermometer is 
reading ~20C low, then the "emergency" shutdown is not going to trigger 
until rather hotter than typical.  (And if you do get the magic smoke 
from your microprocessor, you've told HP services, and allowed them to 
decide how to resolve this.)


-- 
Pure Personal Opinion | HoffmanLabs LLC




More information about the Info-vax mailing list