That's because an ac motor at stall looks like a short circuit to
the line. Think of the rotor as a transformer secondary. Not so
troublesome with small motors, but big motors need current
limiting on startup to avoid overload. To do that, they
"rewire" the windings in series at startup to limit the
current to a safe level. Once the motor has spun up, back emf
from the rotor cancels out running current. proportional to
load.
There may still be many star delta systems in use, but modern
practice typically uses a variable speed drive, with an
inverter to provide programmed frequency, ramped voltage and
current, to allow the motor time to spin up to running speed...